Old 09-07-2017, 06:33 AM   #1
Red Sleeper
 
Red Sleeper's Avatar

Name: Red Sleeper
Title: Too Much Time
Status: Not Here
Join Date: Aug 2009
Location: Lone Star State
Member`s Gallery
Posts: 4,582
Compressor Starter Box Wiring

I picked up a 5hp 60 gallon single stage compressor, but it didn't come with the starter box. Previous owner was starting it through the pressure switch, which I'm not a fan of.

I purchased a starter box and now I'm unsure on how/where to exactly hook up wires. Box is mounted, two 110 legs and ground are hooked up, but I'm not sure where to hook up the wires that will run to the pressure switch.

Click the image to open in full size.
Two hots coming in from breaker panel.

Click the image to open in full size.
Top view of the starter. Thinking I'll just run my wires to the open brass terminals on top?

Click the image to open in full size.
Pressure switch.
__________________
Nick J
'14 Silverado LTZ 5.3 4wd
'05 Cummins QCSB 4wd 48re
'91 Cummins w350 5spd
 
Old 10-30-2017, 11:19 PM   #2
Red Sleeper
 
Red Sleeper's Avatar

Name: Red Sleeper
Title: Too Much Time
Status: Not Here
Join Date: Aug 2009
Location: Lone Star State
Member`s Gallery
Posts: 4,582
Bump for some knowledge on wiring this starter.

It's painful not having compressed air.
__________________
Nick J
'14 Silverado LTZ 5.3 4wd
'05 Cummins QCSB 4wd 48re
'91 Cummins w350 5spd
 
Old 10-31-2017, 09:42 AM   #3
thatguy69
 
thatguy69's Avatar

Name: thatguy69
Title: Too Much Time
Status: Not Here
Join Date: Jul 2011
Location: Mansfield Ohio
Member`s Gallery
Posts: 2,023
OK so the pressure switch is what will pull the coil in on your starter. Your pressure switch should have 2 legs of 110v going to one side of contacts on your pressure switch,the other side of the pressure switch contacts will go to the coil on your starter so that once your pressure switch pulls in the contacts from lack of pressure, it pulls the starter coil in. You can pull the 2 legs of 110 off of the hot side of your starter thatre needed to run to the pressure switch. The coil terminals should be labeled A1 and A2

Sent from my SM-N910V using Tapatalk
__________________
1999 Compound 24v Rust Rocket
2008 F350 P24v/Allison
 
Old 10-31-2017, 09:44 AM   #4
thatguy69
 
thatguy69's Avatar

Name: thatguy69
Title: Too Much Time
Status: Not Here
Join Date: Jul 2011
Location: Mansfield Ohio
Member`s Gallery
Posts: 2,023
Also looks like your missing a heater on the left side of your overload, or buss bar. Can't tell what is in there

Sent from my SM-N910V using Tapatalk
__________________
1999 Compound 24v Rust Rocket
2008 F350 P24v/Allison
 
Old 11-01-2017, 08:51 PM   #5
Red Sleeper
 
Red Sleeper's Avatar

Name: Red Sleeper
Title: Too Much Time
Status: Not Here
Join Date: Aug 2009
Location: Lone Star State
Member`s Gallery
Posts: 4,582
Thanks for the information! Makes sense to me. I'll give this a try once I'm back from work travels.

This starter box doesn't have a heater. Does it need one?
__________________
Nick J
'14 Silverado LTZ 5.3 4wd
'05 Cummins QCSB 4wd 48re
'91 Cummins w350 5spd
 
Old 11-01-2017, 09:08 PM   #6
thatguy69
 
thatguy69's Avatar

Name: thatguy69
Title: Too Much Time
Status: Not Here
Join Date: Jul 2011
Location: Mansfield Ohio
Member`s Gallery
Posts: 2,023
Electrical terms of a Heater is something thatll open up the circuit if the compressor pulls to many amps. The missing one is directly above your middle finger in the first picture, the correct side is above your index finger. Also not quite sure what the red wires are doing in there? Anymore questions just ask, I'm not the greatest at explaining things

Sent from my SM-N910V using Tapatalk
__________________
1999 Compound 24v Rust Rocket
2008 F350 P24v/Allison
 
Old 11-02-2017, 07:28 AM   #7
Red Sleeper
 
Red Sleeper's Avatar

Name: Red Sleeper
Title: Too Much Time
Status: Not Here
Join Date: Aug 2009
Location: Lone Star State
Member`s Gallery
Posts: 4,582
The red wires were in the box and already connected when the unit arrived.
Pre-wired from the manufacture.
__________________
Nick J
'14 Silverado LTZ 5.3 4wd
'05 Cummins QCSB 4wd 48re
'91 Cummins w350 5spd
 
Old 11-02-2017, 11:45 AM   #8
thatguy69
 
thatguy69's Avatar

Name: thatguy69
Title: Too Much Time
Status: Not Here
Join Date: Jul 2011
Location: Mansfield Ohio
Member`s Gallery
Posts: 2,023
Starter should've came with a schematic, post it if you get a chance

Sent from my SM-N910V using Tapatalk
__________________
1999 Compound 24v Rust Rocket
2008 F350 P24v/Allison
 
Old 11-02-2017, 12:53 PM   #9
4x4dually
 
4x4dually's Avatar

Name: 4x4dually
Title: Moderator
Status: Not Here
Join Date: Jan 2007
Location: Stillwater, OK
Member`s Gallery
Posts: 31,789
I just now saw this. If you don't get it figured out, holler at me. It's gravy and I don't mind helping ya out.

Pressure switch will be in series with your coil wire. Also, on mine, I put a toggle switch in series with it as well and mounted it through the started enclosure. That way, if I leave for the weekend, I can flip it off. If the tank or hoses develop a leak, it won't run the entire time I'm gone and burn up.
__________________
Jory 2009 4x4 3500 MCLB

"There are people far less intelligent than you making a living doing this stuff." - Jeff Mumau
 
Old 11-02-2017, 12:55 PM   #10
4x4dually
 
4x4dually's Avatar

Name: 4x4dually
Title: Moderator
Status: Not Here
Join Date: Jan 2007
Location: Stillwater, OK
Member`s Gallery
Posts: 31,789
Like this. If your coil is 120 vac, then it will return to neutral instead of L2.

Click the image to open in full size.
 
Old 11-02-2017, 12:57 PM   #11
4x4dually
 
4x4dually's Avatar

Name: 4x4dually
Title: Moderator
Status: Not Here
Join Date: Jan 2007
Location: Stillwater, OK
Member`s Gallery
Posts: 31,789
Is it a 110 or 220 motor? The starter picture you posted is missing a heater. Gonna need that to run 220 VAC. The silver thing at the bottom. I call them heaters...they are thermal overloads.

Opps. Just noticed I was beat to it.

Quote:
Originally Posted by thatguy69 View Post
Also looks like your missing a heater on the left side of your overload, or buss bar. Can't tell what is in there

So, in that diagram, if the thermal overloads (heaters) get hot, they melt the solder inside allowing the little doo-dad inside to spin and trip the OL (overload) contact. You'll notice it is wired in series with the coil. This if your motor protection from over-current. To reset, just push the red bar that says "reset."

Last edited by 4x4dually; 11-02-2017 at 01:00 PM.
 
Old 11-02-2017, 02:16 PM   #12
thatguy69
 
thatguy69's Avatar

Name: thatguy69
Title: Too Much Time
Status: Not Here
Join Date: Jul 2011
Location: Mansfield Ohio
Member`s Gallery
Posts: 2,023
Starter says it's a 220 coil. I just assumed his motor is wired for 5hp. But your right it could be 110 also

Sent from my SM-N910V using Tapatalk
__________________
1999 Compound 24v Rust Rocket
2008 F350 P24v/Allison
 
Old 11-02-2017, 02:29 PM   #13
zstroken
 
zstroken's Avatar

Name: zstroken
Title: For $$$ your name here
Status: Not Here
Join Date: Sep 2006
Location: Western Michigan(by the lake)
Member`s Gallery
Posts: 23,151
I believe since it is a 220V single phase motor you would only need 1 heater(installing the 2nd heater won't hurt anything but it isn't needed), you can just put a jumper in place on the other side.
__________________
2008 4x4 Megacab, 68RFE
97 Dodge gone....
24V P-Pump Mafia member #1(retired)

Thanks to Mumau Diesel, Goerend Transmission, Northeast Diesel Service!

Last edited by zstroken; 11-02-2017 at 02:31 PM.
 
Old 11-02-2017, 02:48 PM   #14
4x4dually
 
4x4dually's Avatar

Name: 4x4dually
Title: Moderator
Status: Not Here
Join Date: Jan 2007
Location: Stillwater, OK
Member`s Gallery
Posts: 31,789
Quote:
Originally Posted by zstroken View Post
I believe since it is a 220V single phase motor you would only need 1 heater(installing the 2nd heater won't hurt anything but it isn't needed), you can just put a jumper in place on the other side.
You can jumper it, yes. Just wanted him to realize when he turned it on and it didn't work that not matter what he did.....it wouldn't move.

"Current can't jump....and open circuit."

We had an EET instructor back in our first semester for ECT1104. This was fall of '92 at Ok State University. It was "intro to electronics" class and I think his name was Richard Zmich (sp?) or something. Anyways...he was a big ol' boy. Very, very, large man. He would ask something like "what is the current through R1?" with a diagram on the board that had an open in the circuit. Some of the kids would start doing math in their heads and blurt out some retarded answer. He would squat down, then lung forward at warp .00000000048 speed and jump a few 12" floor tiles. When he would land, it seemed like the entire Engineering North building would shake since we were on the 4th floor. I'm sure the fine folks in the classroom under us crapped their pants and thought the unibomber convention was in town. He would always follow his little jump with "Current can't jump....and open circuit!"

Never in my life will I forget that. It was one of those brilliant teaching aids.
 
Old 11-02-2017, 02:52 PM   #15
zstroken
 
zstroken's Avatar

Name: zstroken
Title: For $$$ your name here
Status: Not Here
Join Date: Sep 2006
Location: Western Michigan(by the lake)
Member`s Gallery
Posts: 23,151
Quote:
Originally Posted by 4x4dually View Post
You can jumper it, yes. Just wanted him to realize when he turned it on and it didn't work that not matter what he did.....it wouldn't move.

"Current can't jump....and open circuit."

We had an EET instructor back in our first semester for ECT1104. This was fall of '92 at Ok State University. It was "intro to electronics" class and I think his name was Richard Zmich (sp?) or something. Anyways...he was a big ol' boy. Very, very, large man. He would ask something like "what is the current through R1?" with a diagram on the board that had an open in the circuit. Some of the kids would start doing math in their heads and blurt out some retarded answer. He would squat down, then lung forward at warp .00000000048 speed and jump a few 12" floor tiles. When he would land, it seemed like the entire Engineering North building would shake since we were on the 4th floor. I'm sure the fine folks in the classroom under us crapped their pants and thought the unibomber convention was in town. He would always follow his little jump with "Current can't jump....and open circuit!"

Never in my life will I forget that. It was one of those brilliant teaching aids.

Understood, someone else had pointed out the missing heater as well. Just didn't want the guy searching hi and low for a heater, when he could jumper it. Well technically there is current across the open, however we can't measure it . So we round down to 0
__________________
2008 4x4 Megacab, 68RFE
97 Dodge gone....
24V P-Pump Mafia member #1(retired)

Thanks to Mumau Diesel, Goerend Transmission, Northeast Diesel Service!
 
Old 11-02-2017, 02:57 PM   #16
4x4dually
 
4x4dually's Avatar

Name: 4x4dually
Title: Moderator
Status: Not Here
Join Date: Jan 2007
Location: Stillwater, OK
Member`s Gallery
Posts: 31,789
Quote:
Originally Posted by zstroken View Post
Understood, someone else had pointed out the missing heater as well. Just didn't want the guy searching hi and low for a heater, when he could jumper it. Well technically there is current across the open, however we can't measure it . So we round down to 0
Yes, yes, round down to zero. You get more literal than some of the old crusty analog guys around here that feed us that kind of schidt on a regular basis.
 
Old 11-02-2017, 08:51 PM   #17
thatguy69
 
thatguy69's Avatar

Name: thatguy69
Title: Too Much Time
Status: Not Here
Join Date: Jul 2011
Location: Mansfield Ohio
Member`s Gallery
Posts: 2,023
So you guys are assuming that both poles in the motor are pulling the same amps, so it's ok to only use overcurrent protection on one leg? If that's the case why do you fuse all 3 legs of a 3 phase motor instead of fusing just 1 leg and putting pipe nipples for fuses on the other 2 legs?

Sent from my SM-N910V using Tapatalk
__________________
1999 Compound 24v Rust Rocket
2008 F350 P24v/Allison
 
Old 11-02-2017, 08:58 PM   #18
zstroken
 
zstroken's Avatar

Name: zstroken
Title: For $$$ your name here
Status: Not Here
Join Date: Sep 2006
Location: Western Michigan(by the lake)
Member`s Gallery
Posts: 23,151
Quote:
Originally Posted by thatguy69 View Post
So you guys are assuming that both poles in the motor are pulling the same amps, so it's ok to only use overcurrent protection on one leg? If that's the case why do you fuse all 3 legs of a 3 phase motor instead of fusing just 1 leg and putting pipe nipples for fuses on the other 2 legs?

Sent from my SM-N910V using Tapatalk
If you look at the 220V motor it is a single phase(yes it can be two legs of 120V). So yes one overload would work. Properly done motor circuits(not some 1/8 HP motor or oddball), a motor circuit protector(no thermal trip unit) or a fuses with time delay for short circuit protection, and the overloads protect for "overload" conditions. If you see some old motor circuits used to only have overloads on 2 of the 3 phases.

I have seen applications where people will use a magnetic/thermal breaker on a motor circuit, but for it to be done properly it should be a mag trip motor circuit protector for short circuit protection and then the overloads protect for an overload condition.
__________________
2008 4x4 Megacab, 68RFE
97 Dodge gone....
24V P-Pump Mafia member #1(retired)

Thanks to Mumau Diesel, Goerend Transmission, Northeast Diesel Service!

Last edited by zstroken; 11-02-2017 at 09:01 PM.
 
Old 11-02-2017, 09:29 PM   #19
zstroken
 
zstroken's Avatar

Name: zstroken
Title: For $$$ your name here
Status: Not Here
Join Date: Sep 2006
Location: Western Michigan(by the lake)
Member`s Gallery
Posts: 23,151
Quote:
Originally Posted by thatguy69 View Post
So you guys are assuming that both poles in the motor are pulling the same amps, so it's ok to only use overcurrent protection on one leg? If that's the case why do you fuse all 3 legs of a 3 phase motor instead of fusing just 1 leg and putting pipe nipples for fuses on the other 2 legs?

Sent from my SM-N910V using Tapatalk

I didn't get to respond to the question about the pipe nipples, but it is the same theory, the fuses protect for short circuits, and the overloads protect for overloads. Any leg of a 3 phase circuit can have a short circuit, so you need short circuit protection on individual legs.
__________________
2008 4x4 Megacab, 68RFE
97 Dodge gone....
24V P-Pump Mafia member #1(retired)

Thanks to Mumau Diesel, Goerend Transmission, Northeast Diesel Service!
 
Old 11-03-2017, 07:13 AM   #20
4x4dually
 
4x4dually's Avatar

Name: 4x4dually
Title: Moderator
Status: Not Here
Join Date: Jan 2007
Location: Stillwater, OK
Member`s Gallery
Posts: 31,789
If both legs of a single phase motor aren't pulling the same amount of amps...then there is something wrong. It "is" possible. For instance, if a winding starts shorting or some oddball crap, so it is advised to run both thermal overloads. We were merely stating that he could jumper it if he wanted to so he could get it running. On a three phase, you could protect two out of the three if you wanted....but no one in their right mind would do it that way. You wouldn't believe the amount of Nigerian rigged schidt that shows up while doing service calls. It always amazed me what people thought was ok.
 
Closed Thread

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 09:55 AM.

 


Powered by vBulletin
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2006 - 2024, CompetitionDiesel.com
all information found on this site is property of www.competitiondiesel.com